Greetings,
I have a situation in which a manufacture is tell me..."this is the way it always has been done".
The panel is to control a compressor unit.
1. Compressor Motor is 100Hp
2. Exhaust fan is 5Hp.
3. Power supply (460VAC to 24VDC/10amps)
Ok here is my question and senerio:
The incomming power is to be connected to a distribution block (correctly sized for the 100Hp motor and then some). The Vendor uses 6 AWG wire to run from the distrbution block to the Motor Starter Coil (M1); the wires are unlabeled but you can see the short run in the panel.
Also from the distribution block a branch circuit is ran from to the Power Supply (240VA) using 16AWG (I noted there was no short circuit protection or fault protection). Vendor tried to tell me that it was my responsibiltiy through the disconnect I provided to the panel.
To continue; The vendor came off the "M1" and branched to a fuse block and then to a Motor Over Load (2MOL) and then to the 5HP Fan Motor
The other parallel connection from M1 was to a Motor Over Load (1MOL) and then to a 100HP Motor.
What I do not understand is how can the manufacture get away with calling my disconnect short circuit and fault protection for the Power Supply and the 100Hp motor and any burn up is my responsiblity? Are these both not code violations or am I reading the code incorrectly?
Mary
I have a situation in which a manufacture is tell me..."this is the way it always has been done".
The panel is to control a compressor unit.
1. Compressor Motor is 100Hp
2. Exhaust fan is 5Hp.
3. Power supply (460VAC to 24VDC/10amps)
Ok here is my question and senerio:
The incomming power is to be connected to a distribution block (correctly sized for the 100Hp motor and then some). The Vendor uses 6 AWG wire to run from the distrbution block to the Motor Starter Coil (M1); the wires are unlabeled but you can see the short run in the panel.
Also from the distribution block a branch circuit is ran from to the Power Supply (240VA) using 16AWG (I noted there was no short circuit protection or fault protection). Vendor tried to tell me that it was my responsibiltiy through the disconnect I provided to the panel.
To continue; The vendor came off the "M1" and branched to a fuse block and then to a Motor Over Load (2MOL) and then to the 5HP Fan Motor
The other parallel connection from M1 was to a Motor Over Load (1MOL) and then to a 100HP Motor.
What I do not understand is how can the manufacture get away with calling my disconnect short circuit and fault protection for the Power Supply and the 100Hp motor and any burn up is my responsiblity? Are these both not code violations or am I reading the code incorrectly?
Mary