430.24 gives the rules for sizing conductors supplying several motors. Pretty much the same as it ever was (in a nutshell); 125% of the largest motor plus all the other motors. Fine. But what if the largest motor is on a VFD? If 430.122 requires us to size conductors for the rated input current of the power conversion device instead of the motor full-load amps, why isn't that stipulated in 430.24 as well?
For example, if I have a multi-motor feeder to (2) 10HP ATL starters and a 60HP-rated drive feeding a 50HP motor. Do I use 50HP as the largest motor or 60HP (the rating of the drive)?
For example, if I have a multi-motor feeder to (2) 10HP ATL starters and a 60HP-rated drive feeding a 50HP motor. Do I use 50HP as the largest motor or 60HP (the rating of the drive)?