Gentlemen,
I am a bit confused about the OCPD for more than one motors on a VFD. By the NEC, do I have to provide fuses + O/L for every motors or I only have to provide O/L on every motors ?
Thanks
I'd provide an overload and a contactor for every motor but I don't know what the NEC mandates.Gentlemen,
I am a bit confused about the OCPD for more than one motors on a VFD. By the NEC, do I have to provide fuses + O/L for every motors or I only have to provide O/L on every motors ?
Thanks
I'd provide an overload and a contactor for every motor but I don't know what the NEC mandates.
I'd provide an overload and a contactor for every motor but I don't know what the NEC mandates.
To disconnect the motor that had an overcurrent fault whilst letting the others continue running. We've done this for steel mill roller tables where many motors are connected to one VFD.why would you add a contactor?
The little MPS devices will do that too, and preclude the ability to easily remotely re-engage them while the drive is running. Using the MPS devices requires (if properly designed) that the cabinet be opened to reset them, which ostensibly means the power to the drive was killed first in order to open the door. Of course any of that can be defeated, but anyone working that hard at it would (hopefully) understand the risks of re-energizing a motor when the VFD is already running. You can do that with contactors as well by controlling the coil circuitry, and I imagine you (Besoeker) have the experience to make sure that happens correctly, but in general I don't trust end users that much and I do what I can to make sure that risk is mitigated in a more passive way.To disconnect the motor that had an overcurrent fault whilst letting the others continue running. We've done this for steel mill roller tables where many motors are connected to one VFD.
MPS is a term I'm famaliar with. A link might be helpful.The little MPS devices will do that too
MPS is a term I'm famaliar with. A link might be helpful.
The contactor and thermal overload is usually a cheaper solution.View attachment 15886
http://literature.rockwellautomation.com/idc/groups/literature/documents/pp/140m-pp004_-en-p.pdf
In your world you likely call them something else, such as "circuit breakers", but over here that term has a specific definition and those devices don't meet that, so almost every mfr has a different term for them. Motor Protective Switch (MPS); Motor Starter Protector (MSP); Motor Circuit Protector (MCP, although that also has another meaning and is a trade name); Motor Protection Circuit Breaker (MPCB); Manual Motor Starter (MMS); etc.
If no additional control circuit is needed maybe not.The contactor and thermal overload is usually a cheaper solution.
If no additional control circuit is needed maybe not.
I agree that may be worth consideration, but you still have multiple units to wire either way, the manual motor starter or whatever you decide to call it only needs line in and line out - no controls unless you want to signal the drive or other device that it has tripped.these days you can get a 1/4 HP drive for not much more than $100. Might be less expensive overall to go that direction rather than screw around with extra overloads, extra contactors, and extra wiring.
I agree that may be worth consideration, but you still have multiple units to wire either way, the manual motor starter or whatever you decide to call it only needs line in and line out - no controls unless you want to signal the drive or other device that it has tripped.
We almost always had 110Vac or 24Vdc controls. And sometimes both.If no additional control circuit is needed maybe not.
The application would dictate how important such feedback is necessary. I have one place I put multiple cooling fans for a process on a single VFD. Product is cooled on an open table by wall mounted fans - if one should quit it isn't too detrimental to the process and the operators will notice it isn't running, they may just increased the speed of the others a little to compensate until the problem is resolved.I think you would want some kind of feedback that something has tripped. last time I used some of the manual motor protectors or whatever the heck they are, they were like $60 each. They were ABs so they might have been more expensive than some other brand but they are not cheap.