I have 4 set of 350 MCM parallel service conductors, which are tapped to main service tap Pull box with lug landings.This set is feeding a 1200A Switchboard with 1200A Main CB.The conduit runs are Non Metalic conduit(PVC) from Pull Box to Main Switchboard.From same Tap Pull Box also I am getting one set of Feedes to a 400A Switchboard with400A CB.I am bonding the neutral in each switchboard based on their Largest Feeder Cables.Do I need to bond the neutral in Tap pull box where the Lug landings are,or at each switchboard
Bonded neutral is OK.By bonding I mean Neutrals are bonded to water pipe and Ufer Ground.Do I need to run Equipment ground conductor in service Conduits back to Tap box where service conductors are originated.
Since these two services are fed from same Service Tap Pull Box with PVC conduit,how do I have to approach to size the GEC (Ufer Ground and CW Pipe),also,where I should Bond the neutral to comply with 250-52,250-66.
The tap pull box is fed by 3 sets of 750 Kcmil Over Head service Conductors per phase.
Thanks
Thanks