I have 116,280 watts so what i did was :
116,280VA - 30,000VA = 86,280VA x .4 = 34,512 + 30,000VA = 64,512VA / 240V = 268.8 A or 300A service
Upsize to 400A for future work (adding a garage that a business will use later) so we can just add another meter, tap the 400A conductors, and trench from the meter to said garage.
Now the next issue is multi gang meter sockets have been willed out of existence by the electrical demons so I have to build my own contraption. Maybe I’ll build a box around the wires with 2x4s. But it sounds like I’m gonna have to run to run 400 amp wires to a gutter and come out of the gutter with 3 meter sockets and come out of the 3 meter sockets to 3 100A breaker enclosures and come out of each of them with SER.
My question with this now is going to be how do I run 500 mcm cu x 3 into a gutter and then connect each of them to 4 #2s that can then go down to the meters (I would keep the 4th set of wires in the gutter for future attachment). Could I just run each of the wires the length of the gutter and just grab onto each at various locations with Ilsco insul—eaters? And also, the poco requires bonding bushings at all of these locations but the GEC is 1/0 cu. Surely I don’t have to run that around to all the bushings. Anyone know if I can treat it like ground rods and run #6 cu to the bonding bushings?