I know this is a vague question so bare with me. Can you burn up a generator by hooking up the wrong voltage. Example: 120/240 to a 277/480 and vice versa.
I know this is a vague question so bare with me. Can you burn up a generator by hooking up the wrong voltage. Example: 120/240 to a 277/480 and vice versa.
First off I have never tried it but I wouldn't think the generator would be harmed because it should have overcurrent protection (circuit breaker ).
If you were to hook up the wrong voltage I would think that you could destroy lots of other equipment.
FWIW, the overcurrent protection built into a generator (circuit breaker) may not even trip immediately at the maximum short circuit current the generator can produce.
The vague part is how you hook up voltage to a generator that is, itself, supposed to be the thing that is creating the voltage. Can you explain a bit?
+1
Or it may not trip at all, due to the inability of the genset to deliver sufficient current to trip the genset OCPD before the fireworks begin.
Please provide more info on your installation.I can understand possibly replacing the control panel and wire. But what about replacing the coils or it damaging the entire generator?
I meant hooking up a certain voltage generator to a certain voltage service. Ex: 124/240 generator to a 277/480 service.
Unless you have a paralleling system, or a closed transition transfer switch the generator is never directly connected to the utility voltage. In either case the controls should not permit the contactors to close and connect the generator to the utility if the votlages are not the same.I meant hooking up a certain voltage generator to a certain voltage service. Ex: 124/240 generator to a 277/480 service.