Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
I have a 12-3 multi wire Romex with two hots and a shared neutral and a ground. The NM Cable red wire goes to one 20 ampere breaker ant main panel and the same cables black wire to a different 20 ampere breaker. Red and black go to a separate GFCI Hot terminal on their line side terminals
However there is only one neutral out of multi wire branch circuit NM cable so the single neutral FROM PANEL NEUTRAL BUS goes to first GFCI neutral line side
But do I pigtail this neutral from line side at first GFCI and connect to the next GFCI down stream and on another circuit to its neutral terminal on line side? load side seems wrong and previous install had two hots and one neutral for two circuits with one GFCI which had stopped working
I’m thinking any additional receptacles on load side of GFCIs will force me to have to add at least one more neutral in emt conduit downstream of GFCIs for load side terminals?
Normally separate circuits must have their own neutral in NEC 300 except for multi wire branch circuits I believe?
GFCI tripped but I will look into this tomorrow
However there is only one neutral out of multi wire branch circuit NM cable so the single neutral FROM PANEL NEUTRAL BUS goes to first GFCI neutral line side
But do I pigtail this neutral from line side at first GFCI and connect to the next GFCI down stream and on another circuit to its neutral terminal on line side? load side seems wrong and previous install had two hots and one neutral for two circuits with one GFCI which had stopped working
I’m thinking any additional receptacles on load side of GFCIs will force me to have to add at least one more neutral in emt conduit downstream of GFCIs for load side terminals?
Normally separate circuits must have their own neutral in NEC 300 except for multi wire branch circuits I believe?
GFCI tripped but I will look into this tomorrow