im running 12 120v lighting circuits sharing 4 neutrals from a 208-120 panel. how many egc's do i need?
im running 12 120v lighting circuits sharing 4 neutrals from a 208-120 panel. how many egc's do i need?
One per raceway or multi-conductor cableHow many raceways and type of raceway?
You do realize that the 12 current carrying conductors you are already installing are only good for 50% of their 90 deg rating and if you add 8 more it will even be less don't you?1 2" emt. room for additional circuits.