sparky55

New member
Is there a requirement for the panel front to be labeled to identify that the panel has Multi-wire branch circuits? If so, is it a "WARNING" or "DANGER" label?
 

iwire

Moderator
Staff member
Location
Massachusetts
sparky55 said:
Is there a requirement for the panel front to be labeled to identify that the panel has Multi-wire branch circuits?

No, there is no requirement for that.

Almost all panels have multiwire branch circuits from them.
 

peter d

Senior Member
Location
New England
Ryan, I realize that. I'm just trying to get at what seems to be the heart of the issue, which is an unjustified fear of MWBC's.
 

iwire

Moderator
Staff member
Location
Massachusetts
ryan_618 said:
Yes...but the question was about branch circuits, not feeders and service conductors. :)

Yes, but if that panel supplies an electric range and / or oven it has multiwire branch circuits.

That being the case almost all panels would end up with another meaningless 'Danger Will Robinson' label.
 