I have a question about an existing 120v 20 amp mult-wire branch circuit in a single family residence. The circuit is fed from two 20 amp two single pole breakers with no breaker tie with a 12-3 romex. The 12-3 romex then goes into the first single gang box where the red wire and white wire are backstabed on the receptacle. There is also 12-2 romex that terminates in this box and then goes to another outlet receptacle. The black of the 12-3 and the black of the 12-2 are spliced together, and the white of 12-2 is backstabbed on the receptacle as well.
1. I don’t like backstabbing receptacles, and think the white wires should be spliced with a pigtail to the neutral of the receptacle
2. Do the breakers need to be on different phases, and do they need a breaker tie? (Someone told me that you only need a breaker tie when the multiwire terminates on two yokes of a duplex receptacle, is that true?)