In a multi wire branch circuit 120/240 one wire pulls 15 amps the other wire pulls 2 amps and the neutral pulls 13 amps must i count the neutral as a current caring conductor ? what code article 2008. and it change in the 2014 code?
No. You need not count the neutral because it is carrying the difference in the currents in the two hot wires. The Code treats all the wires in a MWBC as a group and looks at the total amperage. So in this case you see 15+2+13=30 which is the equivalent of two wires carrying 15 each and the third wire 0. This is not how you arrive at the number of Current Carrying Conductors, but it is the motivation behind the rule.
:?
That does not work with all MWBCs, consider a MWBC in a conduit phase A, phase C and neutral. How many CCCs are there?
Or a MWBC supplying non-linear loads?
I think the OP is better off looking at the code sections Rob posted.
I agree with that part.You need not count the neutral because it is carrying the difference in the currents in the two hot wires.
I disagree with that part. In this case, what you see is 15 - 2 = 13 (or if you prefer, 15 - 2 - 13 = 0). You have a 15 amp load on one phase, and a 2 amp load on the other phase, and the net result (net imbalance) is the 13 amps in the neutral. If instead of the proposed loading you really did have a 15 amp load on each phase, you would not see 15 + 15 = 30, but rather 15 - 15 = 0. The 15 amps that leave the source on phase A will return to the source on phase B. They are the same 15 amps of current. They don't add up, and you don't see a "total" of 30 amps.So in this case you see 15+2+13=30 which is the equivalent of two wires carrying 15 each and the third wire 0.
I agree with that part.
I disagree with that part. In this case, what you see is 15 - 2 = 13 (or if you prefer, 15 - 2 - 13 = 0). You have a 15 amp load on one phase, and a 2 amp load on the other phase, and the net result (net imbalance) is the 13 amps in the neutral. If instead of the proposed loading you really did have a 15 amp load on each phase, you would not see 15 + 15 = 30, but rather 15 - 15 = 0. The 15 amps that leave the source on phase A will return to the source on phase B. They are the same 15 amps of current. They don't add up, and you don't see a "total" of 30 amps.
In the case of a partial three phase MWBC, the code states that the neutral is to be counted as a CCC, and wire current and heating analysis comes to exactly the same result. I do not see any conflict in that scenario.1) The situation that the OP gave us was 120/240 voltages -- not possible for a partial 3-phase MWBC.
2) A MWBC serving non-linear loads would have a higher than expected neutral current. That is why the neutral is counted as a CCC in that case. Once again the OP stated the currents in the three conductors as 15, 2, & 13, which indicated the vector and arithmetic answers were the same hence no triplens.
That much is true.The heating effect of the current is the same no matter the "direction". The rules about Ampacity Adjustments are about heating.
That part is not true. The heating effect (from I^2R) of a pair of conductors, each carrying 15 amps, is (2) times (15^2) times (R), or a total of (450)(R). The heating effect of a single conductor carrying 30 amps is (1) times (30^2) times (R), or a total of (900)(R).In your 15-15 case the effective heating is 30.
That much is true.
That part is not true. The heating effect (from I^2R) of a pair of conductors, each carrying 15 amps, is (2) times (15^2) times (R), or a total of (450)(R). The heating effect of a single conductor carrying 30 amps is (1) times (30^2) times (R), or a total of (900)(R).
And that in a 2 out of 3 plus neutral three phase MWBC the heating in the neutral will be exactly the same as in each of the two line wires because that MWBC cannot be balanced with the third phase missing.OK, I see what you are saying.
Thanks for pointing out the heating to me. I guess what it does say is that with a neutral load the heating is going to be less than that of the maximum heating from a full capacity balanced load.
Neutral Conductors:
Here's some examples of when to count and not count the neutral as a current carrying conductor or CCC:
3?- 208Y/120 or 480Y/277 volt system-different circuit types:
A) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
B) 3 wire circuit w/ 2 ungrounded, 1 neutral = 3 CCC's
C) 4 wire circuit w/ 3 ungrounded, 1 neutral = 3 CCC's*
Notes:
A) A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
B) In this circuit the neutral current will be nearly equal to the current in the ungrounded conductors so the neutral counts as a CCC
C) In this circuit the neutral will only carry the imbalance of the current between the three ungrounded conductors so it is not counted as a CCC, with an exception, *if the current is more than 50% nonlinear (see below for NEC article 100 definition) then the neutral would count as a CCC.
1?- 120/240 volt system-different circuit types:
D) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
E) 3 wire circuit w/ 2 ungrounded, 1 neutral = 2 CCC's
Notes:
D) A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
E) In this circuit the neutral will only carry the imbalance between the two ungrounded conductors so the neutral is not counted as a CCC.
Nonlinear Load. A load where the wave shape of the steady-state current does not follow the wave shape of the applied voltage.
Informational Note: Electronic equipment, electronic/electric-discharge lighting, adjustable-speed drive systems, and similar equipment may be nonlinear loads.
That much is true.
That part is not true. The heating effect (from I^2R) of a pair of conductors, each carrying 15 amps, is (2) times (15^2) times (R), or a total of (450)(R). The heating effect of a single conductor carrying 30 amps is (1) times (30^2) times (R), or a total of (900)(R).
You would have to run the numbers. Typically the resistance of the parallel conductors will be greater than that of a single conductor that will carry the same amount of current.So your saying if i parallel conductors i get less heat?
You would have to run the numbers. Typically the resistance of the parallel conductors will be greater than that of a single conductor that will carry the same amount of current.
The heat comparisons in this thread have all been based on conductors of the same size so that they would have the same resistance per foot.
If you have a 360 amp load and use parallel 3/0s in place of a single 500 kcmil, you would have ~5.3 watts of heat per foot of the paralleled 3/0s (2.65 watts for each of the two conductors) and ~3.5 watts per foot for the single 500 kcmil.
Practically speaking, replacing single conductor by parallel conductors stipulates equal votage drops (for the same current) and so equal watts loss.You would have to run the numbers. Typically the resistance of the parallel conductors will be greater than that of a single conductor that will carry the same amount of current. The heat comparisons in this thread have all been based on conductors of the same size so that they would have the same resistance per foot.If you have a 360 amp load and use parallel 3/0s in place of a single 500 kcmil, you would have ~5.3 watts of heat per foot of the paralleled 3/0s (2.65 watts for each of the two conductors) and ~3.5 watts per foot for the single 500 kcmil.
That does not happen under the rules of the NEC.Practically speaking, replacing single conductor by parallel conductors stipulates equal votage drops (for the same current) and so equal watts loss.
You have to remember that the NEC ampacity tables are very conservative.Practically speaking, replacing single conductor by parallel conductors stipulates equal votage drops (for the same current) and so equal watts loss.