Multi Wire GFCI/AFCI

Status
Not open for further replies.

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
I have an existing multi wire 12/3 circuit to a kitchen that is not being touched except for new receptacles. 1 leg feeds kitchen counter top outlets. 2d leg feeds the refrigerator. 2014 code.

So if i am reading this right I shouldn't need AFCI because it's existing correct? So is a two pole GFCI breaker the way to go? Or a two pole combination so they would have AFCI? The panel is GE with THQL breakers if that matters

Right now the have 1 leg fed from the main panel and the other leg fed from a sub panel(generator) which I have to fix anyhow
 

rc/retired

Senior Member
Location
Bellvue, Colorado
Occupation
Master Electrician/Inspector retired
Look at section 406.4(D). That tells you what is required when replacing outlets.

Disclaimer: I did not answer the above post just to hit my 100th post to reach senior member status. 😀

Ron
 