Multi-wire Homerun in the Kitchen(SA)

Status
Not open for further replies.

jpg

Member
A 12/3 w/ground homerun is run into a two device plastic box. This box will hold a GFCI and a single-pole switch. The GFCI will feed two receptacles down-steam. The switch controls the garbage disposal. (Line-side neutrals are madeup and pigtailed.) Is this a code violation?
 

BAHTAH

Senior Member
Location
United States
Re: Multi-wire Homerun in the Kitchen(SA)

As long as the overcurrent device is a 20/2 breaker I would say no violation. You would still need another small appliance circuit. I usually do what you describe except for the disposal and dishwasher using a split wired 20amp duplex receptacle with half switched for the disposal and the other half hot for the dishwasher. Even though your small appliance circuit shares a neutral with the disposal it is still its own circuit and capable of meeting the load requirement for a small appliance circuit.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Re: Multi-wire Homerun in the Kitchen(SA)

Grant, when you say 20/2 do you mean 2-pole breaker? If so why is a 2-pole breaker needed for this application? The 2 circuits are not feeding a common device the way I'm reading the post.
 
A

a.wayne3@verizon.net

Guest
Re: Multi-wire Homerun in the Kitchen(SA)

Curt that is how I read it,as long as the multi wire branch circuit does not supply a device with a common yoke a 2 pole breaker is not required
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Re: Multi-wire Homerun in the Kitchen(SA)

JPG,

A 2 pole breaker is not the way to go here. That rule applies only if the 2 phases are attached to a device on the same yoke (i.e a receptacle with the jumper clip snapped off). However, you should install 2 separate 20 amp breakers (one above the other) so that they are on different phases. That way you won't overload the neutral.
 
Status