- Lockport, IL
- Semi-Retired Electrical Engineer
Existing facility has plans to replace a 40 HP pump with a 100 HP pump. I am told the conduit from power source to motor controller is 1-1/4”. To me it looks like RGS. There is one multi-conductor cable in the conduit, and I am told it is #4. If I replace the cable with a larger one, how do I figure ampacity? Am I right in believing that the NEC tables don’t apply to other than single conductors? How do I interpret the top of Table 310.15(B)(16): "Not more than three current-carrying conductors in . . . cable. . ."? Do I look to manufacturer data for ampacity? I am looking at one web site that tells me their #2 cable (3 conductor plus ground) has an ampacity of 130, and I need 124 for a 100 HP motor. Their table also tells me that this cable has a cross-sectional area that is below 53% of the area of a 1-1/4” RGS. So that barely satisfies the project requirements.
Voltage drop may complicate matters a bit. But is this a realistic approach to this upgrade project? I strongly suspect that replacement of the 1-1/4” conduit will be physically impossible.