We work in a lot of IT closets in MDUs and such, and I can count on one hand the times i've run into a proper ground bar.
In our facilities we always install an main ground bar, and sometimes an auxiliary ground bar as well in another room if we have gear in multiple rooms. We always put up a ground halo overhead and ground every rack. Each rack also has a vertical ground bar from top to bottom that all the servers and network switches are also grounded to. Most of them have ground lugs on them, and they are there for a reason. The majority of IT people don't use them with the argument that its grounded through the "power cord", but our interpretation of 250.110 is that if the equipment is "fastened in place", which it is if screwed into a rack, that it needs to be grounded...and thats why the lug is there in the first place.