I haven't done one of these in quite some time. Just hoping someone can take a quick look at my procedure and see if I left anything out or did something wrong.
The units are town homes and have gas furnaces, gas ranges, and will not get air conditioners.
5 plex individual square footage
1358
1471
1580
1580
1646
7635 – Total square footage
Small appliance branch circuits
1500 * 10 = 15000
Laundry load
1500 * 5 = 7500
Total general lighting 30135
First 3000 @ 100% 27135 @ 35% = 12497
Clothes dryers
5000 * 5 = 25000
25000 @ 85% = 21250
Appliances fastened in place
Dishwasher 960 * 5 = 4800
Disposal 600 * 5 = 3000
Water Heater 4500 * 5 = 22500
Total 30300
30300 @ 75% = 22725
Micro hood
1000 * 5 = 5000
Gas Furnace
1800 * 5 = 9000
Total
12497 General lighting
21250 Clothes dryers
22725 Fixed appliances
5000 Microwaves
9000 Gas furnaces
70472 / 240 = 294 amps
Will install two runs of 4/0 to meter pack
Will install 4/0 SER with 200 amp breaker to each individual unit. Will install main lug 200 amp panel in each unit
The units are town homes and have gas furnaces, gas ranges, and will not get air conditioners.
5 plex individual square footage
1358
1471
1580
1580
1646
7635 – Total square footage
Small appliance branch circuits
1500 * 10 = 15000
Laundry load
1500 * 5 = 7500
Total general lighting 30135
First 3000 @ 100% 27135 @ 35% = 12497
Clothes dryers
5000 * 5 = 25000
25000 @ 85% = 21250
Appliances fastened in place
Dishwasher 960 * 5 = 4800
Disposal 600 * 5 = 3000
Water Heater 4500 * 5 = 22500
Total 30300
30300 @ 75% = 22725
Micro hood
1000 * 5 = 5000
Gas Furnace
1800 * 5 = 9000
Total
12497 General lighting
21250 Clothes dryers
22725 Fixed appliances
5000 Microwaves
9000 Gas furnaces
70472 / 240 = 294 amps
Will install two runs of 4/0 to meter pack
Will install 4/0 SER with 200 amp breaker to each individual unit. Will install main lug 200 amp panel in each unit