Hi, I have a project I am working on, which originally was specified from the electrical room ( multiple meters stack) to unit buildings subpanel feeders rated 100 amps with conduit size 1-1/4" with 3x#4 +1#8 THWN CU. All the switchgear is rated 75 degrees terminations. Now, this is where I am confused if I run NMB cable 4-3 as a feeder. Will this meet code? I am concern about 334.80, where says I need to determine the ampacity in accordance with 310.15, but then say the allowance ampacity shall not exceed the 60 degrees which makes this wire only good for 70 amps. If I consider the 83% factor an adjustment factor, so you can use the 75C table per 310.15(B)(7)(2) this wire is good for 85 amps, or NMB cable needs to be always calculated at 60 degrees.
Thanks,