What table would you use for a 120/240v Single phase Multifamily building? 310.15 b6 list's multifamily as an option. Although M Holt's exam prep answer, stated you need to use Table 310.16.
What table would you use for a 120/240v Single phase Multifamily building? 310.15 b6 list's multifamily as an option. Although M Holt's exam prep answer, stated you need to use Table 310.16.
You would size service conductors per 310.16
For the feeders serving the dwelling units you could use 310.15(B)(6) {presuming only one feeder per unit}
For feeders serving house panels, you use 310.16.