Dub-A-Dub
Member
- Location
- Johnson City,TN
- Occupation
- Engineer
I'm working on 14-units that are housed inside a bigger complex. Each dwelling unit is showing around 111 Amps, using 220.82, and I'm going to install a 125A ML 120/240 1-ph panel in each. I'd like to install a 3-phase panel to serve sub-feed each apartment panel from. The complex has multiple services coming in at 120/208 3-ph. When I use 220.84 to size the feeder to my new main panelboard I'm getting ~360A (111*14*208 = 323kVA --> 323kVA * 0.40 = 129.3kVA --> 129.3kVA / 208V /1.732 = ~360A).
My question is this...I've calculated the feeder based on 220.84 of the NEC, do I now need to multiply by 125% for the conductors and OCPD or can I just round it up to a 400A panel and feeder?