Gave the following to local utility company, want to be sure it is correct.
Multi dwelling 10 units 100 amp meters, 1 common area 200 amp
A/C 4.08kw/unit 40.8KW 40.8
Cooking 12Kw/unit 120.0KW 90.0
Dryer 5kw/unit 50.0KW 25.0
Space Heater 30.6kw 30.6
Water Heater 4kw/unit 40.0KW 40.0
Lighting 2.7kw/unit 27.0KW 27.0
Dishwasher/Garbage disposal 2.4kw/unit 24.0kw 24.kw
Total 331.86KW 277.40KW
70% Total Connected Load 232.30Kw 194.18KW
1st Time not sure about my calculations, I sent the first column but I thought I should sent the second where I reduced each one based on quanitity, than took a further reduction at the end.