We apply demand factors (table 220.84) to feeders/services for units in a multifamily dwellings.
The recent impact of hurricane Irma in FL, has caused developers of high and mid-rise condos to ask whether the planned onsite generator can be upsized to supply a limited number of circuits to each residence unit for refrigeration, one or two receptacles, and a few lights? (the buildings in question are still in various phases of design and development)
It was thought that we might install a small dedicated panel for these emergency circuits which would be fed via an ATS.
My first swag at this was to extract the load from the current dwelling calcs, and apply it separately as a new load on the generator. This caused a discussion/debate about whether I could use a demand factor on these loads?
Can a demand factor be applied to these loads in one instance, and not in another, slightly modified instance?
I do not have a dogmatic opinion about this, if a demand factor cannot be applied, I would like to understand why so I can avoid a similar mistake in the future, and explain why the generator/feeder/service size has increased proportional to the newly added loads.
As a secondary question - I just noticed that 220.84(A)(1) permits the use of the demand factors in table 220.84 as long as the unit has a single feeder.
Does the use of a second feeder for the "emergency" panel in the unit, as described above, remove our ability to apply a demand factor on the normal feeder/service?
Thanks for the input.
The recent impact of hurricane Irma in FL, has caused developers of high and mid-rise condos to ask whether the planned onsite generator can be upsized to supply a limited number of circuits to each residence unit for refrigeration, one or two receptacles, and a few lights? (the buildings in question are still in various phases of design and development)
It was thought that we might install a small dedicated panel for these emergency circuits which would be fed via an ATS.
My first swag at this was to extract the load from the current dwelling calcs, and apply it separately as a new load on the generator. This caused a discussion/debate about whether I could use a demand factor on these loads?
Can a demand factor be applied to these loads in one instance, and not in another, slightly modified instance?
I do not have a dogmatic opinion about this, if a demand factor cannot be applied, I would like to understand why so I can avoid a similar mistake in the future, and explain why the generator/feeder/service size has increased proportional to the newly added loads.
As a secondary question - I just noticed that 220.84(A)(1) permits the use of the demand factors in table 220.84 as long as the unit has a single feeder.
Does the use of a second feeder for the "emergency" panel in the unit, as described above, remove our ability to apply a demand factor on the normal feeder/service?
Thanks for the input.