warriorelectrician
Member
- Location
- Anacortes Washington
I am bidding on some 6plex units and have a few questions. First is the service, the specs. call for two parallel runs of 4-0 with 3-0 neutral on a 350 amp main breaker all grouped together. Now I now you can do this but where does it say you can group more than 6? My next question is the specs are calling to run #2 alum SER to each unit on a 100amp breaker from the service. I have failed this on inspection before because this does not follow under the 310.15 code because he considered the service entrance where the 100amp main breaker was (at the service) outside. Therefore I had to follow 310.16 and run 1-0 ser. Oh yeah 60 degree or 75 degree on the SER wire.
Now I know this could be considered using the entire load per unit but each inspector has his own interpretion. What is yours