I have multiple recepticles inside a mechanic service garage. The owner has a few pieces of equipment that he can plug in to these outlets. All of the equipment are of the same ratings. Right now I have 3 plugs thoughout the shop. One at each bay, he can plug in: High pressure sprayer, wire feed welder, arc welder, plasma cutter, On the normal activity, never will 2 or 3 for that matter will ever be used at the same time. Right now I have them all on the same 50A, 2-pole breaker. All are 3 wire cord, plug connected, from the factory, straight blades. Is this a wrong installation according to the code, but actually the breaker rating is right according to the load being used. He wants to add one more location, which will be a total of 4 locations then, now that seems a little strange but convience is everything. Should I change all recepticles to individual breakers, but remember that I already have a 42 space panel used up, could possibly make room for 2 maybe 4 poles. It is a brand new building less than 2 years old, 200A service. Mechanics garage really doesn't use much power, most everything is air powered, except convience plugs, lights, and welders. Right now all locations have #8 THHN conductors, all with separate raceways, and spliced with approved method in gutter under service panel. Must the conductor size be that of T.630.11(a), 100% of first 2 and 85% for 3rd etc....? I would appreciate any info reguarding any of this!
Thanks-