No demand factor applies unless the equipment is interlocked to not run simultaneously.
220.60 Noncoincident Loads. Where it is unlikely that two or more noncoincident loads will be in use simultaneously, it shall be permissible to use only the largest load(s) that will be used at one time for calculating the total load of a feeder or service.
Well, in theory, I agree. Say for instance an industrial facility where their documented switching program turns some equipment on or off manually by the breaker at different times. But how do you implement this for say a 100 room hotel with PTAC units where the units are never switched off other than thermostatically or by housekeeping but only when the room is vacant?I think that is an overstatement, I think as long as the loads are not likely to run at the same time you are good to go.
Well, in theory, I agree. Say for instance an industrial facility where their documented switching program turns some equipment on or off manually by the breaker at different times. But how do you implement this for say a 100 room hotel with PTAC units where the units are never switched off other than thermostatically or by housekeeping but only when the room is vacant?
Turning one breaker or disconnect off then another on—manually—is a form of electrical interlock... just not the means that comes to mind when the word interlock is mentioned.Fair question but still does not change the fact that the code section only says unlikely, not impossible.
There is nothing requiring electrical interlocking.
Turning one breaker or disconnect off then another on—manually—is a form of electrical interlock... just not the means that comes to mind when the word interlock is mentioned.
The point is, how do you assure the plan checker that one or more loads are non-coincident?Sure it can be, but still no interlock required so I am missing the point.
The point is, how do you assure the plan checker that one or more loads are non-coincident?
You claimed an interlock is required however the NEC does not require an interlock for non-coincidental loads. We can go round and round with different scenarios but in the end an interlock is not NEC mandated. Might be a good idea, might be a good design, it might give a plan checker the warm fuzzies but it is still optional.
Now, am I saying that cppoly can claim 'non-coincidental loads' in this case? No, I think it is likely the AC units would run at the same time unless there is some underlying reason they would not.
For the record, I did not say an interlock was required. I implied it. But it was with respect to the type of circuit I assumed it to be... and I'd wager that I'm correct.You claimed an interlock is required however the NEC does not require an interlock for non-coincidental loads. We can go round and round with different scenarios but in the end an interlock is not NEC mandated. Might be a good idea, might be a good design, it might give a plan checker the warm fuzzies but it is still optional.
Now, am I saying that cppoly can claim 'non-coincidental loads' in this case? No, I think it is likely the AC units would run at the same time unless there is some underlying reason they would not.
Yes, odds are all will not run concurrently most of the time. But there's no way to assure the A/C units will never all run simultaneously if they are just thermostatically controlled.I think the underlying reason they won't all run simultaneously is because they won't, given as they are on thermostats, and some rooms are likely unoccupied and the A/C won't run there at all. However, I don't see any way you can take some kind of "credit" for that because you can't quantify it, unlike other similar situations where the code calculations have quantified it for you.
For the record, I did not say an interlock was required. I implied it. But it was with respect to the type of circuit I assumed it to be... and I'd wager that I'm correct.
I agree interlocking is not required. But you best be able to substantiate to the AHJ a load reduction where not interlocked.
No demand factor applies unless the equipment is interlocked to not run simultaneously.
You two can twist it any way you want but as I said, I did not say an interlock was required.Actually you did state it was required, although you did not use the word "required".
My understanding of sizing heating/cooling units for best overall efficiency and comfort means they will be sized to run quite a bit of the time during the maximum extremes they were designed for. You may not reach those extremes in some areas but a half dozen or less times a year but when you do, or if you exceed the maximum extreme it was designed for the duty cycles run near or at 100%.I think the underlying reason they won't all run simultaneously is because they won't, given as they are on thermostats, and some rooms are likely unoccupied and the A/C won't run there at all. However, I don't see any way you can take some kind of "credit" for that because you can't quantify it, unlike other similar situations where the code calculations have quantified it for you.
Yes, odds are all will not run concurrently most of the time. But there's no way to assure the A/C units will never all run simultaneously if they are just thermostatically controlled.
For the record, I did not say an interlock was required. I implied it. .
But it was with respect to the type of circuit I assumed it to be... and I'd wager that I'm correct
Yes, odds are all will not run concurrently most of the time. But there's no way to assure the A/C units will never all run simultaneously if they are just thermostatically controlled.