aharreld

Member
Location
Montana
Occupation
Electrical Engineer
I'm working with a homeowner who wants the circuits for the gazebo fed from a panel in the house. The gazebo has infrared heaters, receptacles and lighting. The gazebo has a foundation, a floor, and a roof supported by beams, but no walls. The gazebo is located about 150' from the house. My understanding of 225.30 is that the gazebo will require it's own subpanel, since it is a separate structure and will have multiple branch circuits. The homeowner does not want a panel visible on their gazebo.
My questions for you all are:
  • Am I wrong? Can I feed the gazebo with multiple branch circuits?
  • If I'm not wrong, can the subpanel be located detached from the gazebo? If so, how far away?
  • Is the homeowner just SOL and they need to accept a panel on their gazebo or not have heaters in their gazebo?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
1) the code does not permit multiple circuits for this application
2) a means of disconnect is required at the structure either inside or outside the structure nearest the point where the conductors enter. I would not permit a remote panel.
3) they need to accept a panel if they want that number of circuits
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Would a panel in a small enclosure proximal to the gazebo fly?

Likely an AHJ call, but how close would a 'box' need to be to be considered part of the same structure.

-Jon
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
Why no panel? The aesthetics? Can't it be disguised as something else to fit with the time period? I'm guessing this thing has a Victorian theme.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Suggest a stationary bench with a hinged seat like a storage compartment, and put the panel there.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
I was thinking take the cover to a vinal sign or auto wrap place, and have them cover it with a pattern like this, or whatever she likes

c65e68de85f0370f4058f675de99a453.jpg
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
Upsell her some stuff like this


Then she can sit in her gazebo and pretend she is a slightly aged but still ravishingly beautiful Victorian Heiress living in Edwardian times
 

shockdudude

Member
Location
Putnam Valley,ny
Occupation
Electrician
bonus It needs to be a rain tight panel and branch circuits have to wired in uf or thhn wire, put panel outside on back side and don't forget your ground rod, and need main breaker if more than 6 breakers...
 