Multiple branch circuits to remote building

Status
Not open for further replies.

BigMike

Member
I have a client who has a residence with many buildings on his site. He has a garden shed that has numerous electrical panels. About 75' away, there is a guest house. He wants to feed all the guest house lighting/receptacle/HVAC power from panels located in the garden shed. I explained to him it would be more cost effective to place a panel in the guest house, but he doesn't care about cost and wants all his breakers located in one location (The garden shed). What should I do for grounding? (I plan on using a shunt trip pushbutton for a service discconect on the guest house).

Thanks,
Mike
 
The first thing that I think you do is to read 225.30. Then perhaps you should have another conversation with the client.

Your initial suggestion was the right thing to do. Stand by it.
 
Re: Multiple branch circuits to remote building

BigMike said:
I have a client who has a residence with many buildings on his site. He has a garden shed that has numerous electrical panels. About 75' away, there is a guest house. He wants to feed all the guest house lighting/receptacle/HVAC power from panels located in the garden shed.

You might want to take a leisurely stroll through Article 225 before agreeing to do it, paying particular attention to 225.30, :)
 