Guys, I am faced with an unexpected challenge.
I am doing design work in an old school building.
There are seven main lug only electrical panels in the building...most are 40-50 years old, so replacing them, at least on an as needed basis is probably a good idea.
I discovered all of the panels are fed from an 800-amp distribution panel, located outside, approx. 60 feet from the building. The dist. panel has an 800 amp main breaker, and is fed from a utility transformer 10 feet away.
It looks like all of the interior panels were re-fed like this no more than 10 years ago (dist. panel is new...conduits on side of the building are still pretty shiny, etc.)
So by my reasoning, I have a building with seven services to it. I'm not sure I can replace a panel and be grandfathered with existing conditions.
Do you agree I have seven services?
If so, any insights on how to deal with this? At the very least, I would call for a bunch of multiple service labels on all of the panels. That might appease the local inspector (assuming he isn't the inspector who approved this mess when it was built this way).
I am doing design work in an old school building.
There are seven main lug only electrical panels in the building...most are 40-50 years old, so replacing them, at least on an as needed basis is probably a good idea.
I discovered all of the panels are fed from an 800-amp distribution panel, located outside, approx. 60 feet from the building. The dist. panel has an 800 amp main breaker, and is fed from a utility transformer 10 feet away.
It looks like all of the interior panels were re-fed like this no more than 10 years ago (dist. panel is new...conduits on side of the building are still pretty shiny, etc.)
So by my reasoning, I have a building with seven services to it. I'm not sure I can replace a panel and be grandfathered with existing conditions.
Do you agree I have seven services?
If so, any insights on how to deal with this? At the very least, I would call for a bunch of multiple service labels on all of the panels. That might appease the local inspector (assuming he isn't the inspector who approved this mess when it was built this way).