erock1
 - Houston, Tx
So I have multiple hots of the same circuit going through one 3/4 pipe. I some instances I have 3 ways and four ways with 8 and 9 ungrounded wires in it. Does debating apply if it's the same circuit?
			1Number of conductors is the total number of conductors in the raceway
or cable, including spare conductors. The count shall be adjusted
in accordance with 310.15(B)(5) and (6). The count shall not include
conductors that are connected to electrical components but that cannot
be simultaneously energized.
Derating, maybe. Debating, yes. I'd argue that traveler wires cannot be simultaneously energized by design of 3/4 way switches, and even some bizzaro failure would send ~1/2 Amax thru each (and wiring that way intentionally is a violation of paralleling small wires).
I believe the intent of the note is that one traveller as part of a 3 way do not need to be counted. Switch legs do need to be counted