I am designing the installation of several circuits for multiple HVAC rooftop units.
It would be easier to run a single conduit, and install (8) #8 THHN conductors. This would supply power to (4) separate units.
The units have a min. circuit ampacity requirement of 36 Amps, Max breaker of 50.
According to the NEC, #8 THHN is rated for 55 Amps, before derating factors. I figure applying 70% to that amount equals 38.5 Amps. Which should be sufficient for the connected loads.
Section 440.22 allows me to use a 50 Amp breaker on these circuits.
Does anyone concur with my assessment?