Thanks Larry........................that is soooooooooooo true and a good lesson learned. A feeder to a sub panel is the way to go.
Hi All,
I am running 20 #12 circuits in emt, outside, residential, THHN, 45 feet. I have the calc's. Wanna compare notes? Thanks in advance.
40 current carrying conductors = 40 % ampacity therefore to obtain 20 amp you need a #8. 40 # 8's =2.5 inch emt ( 64 allowed in 2.5 but only 36 in a 2 inch) #8 THHN at 90 degrees is 50 amp @40% =20 amp.
....... Why are you running #8 for "#12 circuits"? #8 is overkill for a 12 amp load....:grin:
Table 310.15 (B)(2)(a) if using 31-40 current carrying conductors in a raceway you have to de rate the conductor. Table 310-16 # 12 is rated at 30 amp and @40 % it goes to 12 amp. # 8 is rated at 55 amp and @ 40% goes to 22 amp. I would never do this but got called on a similar situation recently so this is fresh.