Got an inspection on a new service yesterday.
Like for like panel change, so it’s already full.

Inspector mentioned that multiple grounds are allowed in the same hole on a N/G bar, but neutrals need to be 1 per hole. He didn't call me on it or make me change it, just mentioned it.
The manufacturers instructions on the panel cover show the quantities and sizes of conductors allowed per hole, and makes no exceptions for neutrals.
I’ve never seen that in the NEC either.
Like for like panel change, so it’s already full.


Inspector mentioned that multiple grounds are allowed in the same hole on a N/G bar, but neutrals need to be 1 per hole. He didn't call me on it or make me change it, just mentioned it.
The manufacturers instructions on the panel cover show the quantities and sizes of conductors allowed per hole, and makes no exceptions for neutrals.
I’ve never seen that in the NEC either.