Multiple Conductors In Same Hole

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
Got an inspection on a new service yesterday.

Like for like panel change, so it’s already full. 😳🙄

Inspector mentioned that multiple grounds are allowed in the same hole on a N/G bar, but neutrals need to be 1 per hole. He didn't call me on it or make me change it, just mentioned it.

The manufacturers instructions on the panel cover show the quantities and sizes of conductors allowed per hole, and makes no exceptions for neutrals.

I’ve never seen that in the NEC either.
 
EGCs can occupy more than one per hole if the panel mfg allows. Neutrals can never occupy more than one per hole. Someone can post the NEC as I don't have it handy.
 
When there is more than one set of rules to follow, the more restrictive generally applies.
 
This has been in the NEC for many code cycles. Neutrals one per hole. EGC's as many as the listing allows.
And many years before that in the listing instructions making is a 110.3(B) rule. The substantiation for putting into the code was that many installers were not following the requirements of the listing instructions.
 
When I started, it was common practice in my area for the ground and neutral of a circuit to be in the same hole, if it was the main panel. It looked so nice and neat.
 
When I started, it was common practice in my area for the ground and neutral of a circuit to be in the same hole, if it was the main panel. It looked so nice and neat.
That specific install should've been continued. The issue of losing a multiwire nuetral isn't as big of a deal in that then having 2 multiwire nuetrals incase one is moved and the other has a load.
 
When I started, it was common practice in my area for the ground and neutral of a circuit to be in the same hole, if it was the main panel. It looked so nice and neat.
I used to do that as well. Didn't realize (like many others) that the instructions didn't allow it. Did see that most neutral bars were rated for multiple conductors but somehow missed that it only applied for EGC's when they are permitted to land on the neutral bus
 