Multiple conductors through same opening in panel

Status
Not open for further replies.

brian_mller

Member
Location
austin, tx
Been tusseling with a builder out in bubba-land....

I informed the builder that multiple electrical conductors through the same opening in the panels is not allowed...could I be wrong? I don't think I am, but struggle to find it in the NEC.
 

Attachments

  • IMG_0542.jpg
    IMG_0542.jpg
    139 KB · Views: 2
  • IMG_0841.jpg
    IMG_0841.jpg
    135.5 KB · Views: 2
Multiple conductors, and even multiple circuits, in one opening are definitely allowed. And may be good design.
On the other hand NM entering a panel through a sleeve or other opening without a clamp may be a problem. Likely is a problem with the NM runs in your photo. Alsoentially a wire fill and derating issue.
And service conductors cannot share a raceway with non-service (OCPD protected) conductors. Bottom entry point looks fine in that respect.

More thoughts if you can provide more details.

Sent from my XT1585 using Tapatalk
 
The picture is a code violation but it has been an accepted install around here since before I moved here in 1978. It is also common in other states -Arizona, Tx etc...but it is not compliant and is usually done when there is an outdoor panel.
 