charlie b said:There are two issues here.
The second issue is whether it is acceptable to use #4 wire (rated 85 amps) to feed the sub-panel, .
Dexie123 said:Off topic here Charlie. Just trying to get my head around something. When it's said that #4 is good for 85 amps based on 75deg, doesn't 110.14(a) say 4awg should be used for only the 60deg column or does the 3rd point in that article where it says "conductors with higher temp rating if the equiptment is listed and identified for use with such conductors" mean as long as a subpanel (in this case) lugs are identified for 75deg column that 85amps is ok?
Thanks
infinity said:Almost all lugs are now rated for 75 degrees C. 110.14(C)(1)(a)(3) would allow you to use the 75 degree rating for a #4 lug.
I agree with Trevor's answer:Dexie123 said:. . . or does the 3rd point in that article where it says "conductors with higher temp rating if the equiptment is listed and identified for use with such conductors" mean as long as a subpanel (in this case) lugs are identified for 75deg column that 85amps is ok?
infinity said:Almost all lugs are now rated for 75 degrees C. 110.14(C)(1)(a)(3) would allow you to use the 75 degree rating for a #4 lug.
infinity said:Almost all lugs are now rated for 75 degrees C. 110.14(C)(1)(a)(3) would allow you to use the 75 degree rating for a #4 lug.
Riograndeelectric said:OK so what abot lugs in older panels or breakers in older panels marked with40c . so how do you calculate the wire ampacity for 40c. I have often wondered about this when working in older panels. also if there is no temp marking on the panel,lugs or breakers would you then use the 60c rating for calulation purposes?