Question: NEC Tables 310.18 and 310.19 (250C Conductors).
Table 310.19 lists the ampacity for a #2Ga. (250C) wire at 381 Amps. This amperage is based upon a single insulated conductor in free air.
Table 310.18 lists the ampacity (for not more than three current carrying conductors in a raceway) of #2Ga. (250C) wire at 191 Amps.
If I do a correction factor for having (24) #2Ga. wires in a single conduit, do I calculate the new amperage from Table 310.19 (381 Amps) or from Table 310.18 (191 Amps)?
The correction factor for having 24 conductors in a conduit is a .45 multiplier.
"If" I am correct to use the .45 factor calculation with Table 310.19, then my allowable ampacity is 172 Amps.
"If" I am correct to use the .45 factor calculation with Table 310.18, then my allowable ampacity is 86 Amps.