Can I use multiple small contactors in lieu of one big one, if all are controlled by the same button?
The NEC (sec 430)and NFPA79 (sec 9 & 10)require an emergency stop button for a machine containing motors. The normal way is for the E-stop to open a contactor, removing power from the motors, Groups of motors that perform a common function should have a common disconnecting means.
Bottom line, if I have four 25A motors as part of a system, two 60A contactors (tied to two motors each)are cheaper than one 120A contactor (tied to all four). One stop button setup can energize both of the 60A contactor coils in parallel.
Is this within the rules, as long as each individual contactor load times 115% doesn't exceed its rating? I won't put two 60A contactors in parallel and tie all four motors to both. Two motors each.
I don't see anything that says the scheme of two 25A loads on each 60A contactor, with all contactor coils tied to one stop button, is wrong.
Am I OK here?
The NEC (sec 430)and NFPA79 (sec 9 & 10)require an emergency stop button for a machine containing motors. The normal way is for the E-stop to open a contactor, removing power from the motors, Groups of motors that perform a common function should have a common disconnecting means.
Bottom line, if I have four 25A motors as part of a system, two 60A contactors (tied to two motors each)are cheaper than one 120A contactor (tied to all four). One stop button setup can energize both of the 60A contactor coils in parallel.
Is this within the rules, as long as each individual contactor load times 115% doesn't exceed its rating? I won't put two 60A contactors in parallel and tie all four motors to both. Two motors each.
I don't see anything that says the scheme of two 25A loads on each 60A contactor, with all contactor coils tied to one stop button, is wrong.
Am I OK here?