Good morning, I have tried to scroll to find this scenario--but have not found.
I have a customer that is wanting to install (2) Tesla chargers on a shared circuit.
Teslas installation instructions show the optional connection for load sharing.
(One main charger, one slave charger.)
After intial thought, as long as the wiring was installed for the maximum ampacity of the breaker--this would not be an issue.
But, 625.40 says "each outlet installed for the purpose of charging electric vehicles shall be supplied by an individual branch circuit. Each circuit shall have no other outlets."
Outlet is defined as "an outlet is a point on a wiring system that supplies current to utilization equipment"
If installed a junction box with splice point to split between chargers and communication wire as tesla shows, we technically have 'two outlets' therefore would not be permitted?
I would consider a junction box NOT an outlet if I am not connecting a receptacle or switch directly to it---but I am splicing wires to connect to utilization equipment--just not directly in that box?
I have attached teslas installation for load sharing.
**Wisconsin--2017 NEC for reference**
Thanks in advance.
I have a customer that is wanting to install (2) Tesla chargers on a shared circuit.
Teslas installation instructions show the optional connection for load sharing.
(One main charger, one slave charger.)
After intial thought, as long as the wiring was installed for the maximum ampacity of the breaker--this would not be an issue.
But, 625.40 says "each outlet installed for the purpose of charging electric vehicles shall be supplied by an individual branch circuit. Each circuit shall have no other outlets."
Outlet is defined as "an outlet is a point on a wiring system that supplies current to utilization equipment"
If installed a junction box with splice point to split between chargers and communication wire as tesla shows, we technically have 'two outlets' therefore would not be permitted?
I would consider a junction box NOT an outlet if I am not connecting a receptacle or switch directly to it---but I am splicing wires to connect to utilization equipment--just not directly in that box?
I have attached teslas installation for load sharing.
**Wisconsin--2017 NEC for reference**
Thanks in advance.