ron
Senior Member
- Location
- New York, 40.7514,-73.9925
There is a small building being placed on the property which is a distance away from the main building.
They want (3) different type feeders brought to the building. (1) utility only, (1) a feeder from an ATS in the main building which would be utility or gen depending on which is available and lastly (1) UPS feeder.
Does anyone see a problem with bringing three feeders into an outbuilding? The (3) feeders will be terminated into (3) panelboards each with a main breaker. The panelboards will be adjacent to each other.
As long as there are <6 main circuit breakers, is there a problem?
I recall when bringing circuits to a shed at my home, there was an issue with more than one circuit/feeder (although a single multiwire was okay), so we put a small sub-panel with a single main breaker which seemed to make everyone happy. I don't recall the code section that made that an issue.
Thanks
They want (3) different type feeders brought to the building. (1) utility only, (1) a feeder from an ATS in the main building which would be utility or gen depending on which is available and lastly (1) UPS feeder.
Does anyone see a problem with bringing three feeders into an outbuilding? The (3) feeders will be terminated into (3) panelboards each with a main breaker. The panelboards will be adjacent to each other.
As long as there are <6 main circuit breakers, is there a problem?
I recall when bringing circuits to a shed at my home, there was an issue with more than one circuit/feeder (although a single multiwire was okay), so we put a small sub-panel with a single main breaker which seemed to make everyone happy. I don't recall the code section that made that an issue.
Thanks