Multiple Fire Pumps on Single Transformer

Woobie

Member
Location
Los Angeles, CA
Occupation
Electrical Engineer
Does the NEC, NFPA 20, or common sense prohibit multiple Fire Pumps from being fed off a single service-tapped transformer? I know code want's a "dedicated feeder," but I'm not sure if this situation falls under that or some other clause that I'm not seeing.

More details on the situation:

There's an existing medium voltage service feeding a two-building campus. The service lineup has a separate tap + fused disconnect ahead of the main MV disconnect. That disconnect feeds a step-down transformer (in the same service lineup) and one existing Fire Pump.
Due to a site reconfiguration, there is now a need for two separate fire pumps (each feeding a separate building). We'd like to avoid using diesel fire pumps and definitely want to avoid tapping into the service bus. I'm wondering if it'd be allowed to - given physical feasibility - double-lug the FP transformer and provide a separate feeder from the transformer secondary to each fire pump controller (two total).

Thanks!
 
Art 695.3 only requires the supply be from a "reliable" power source.
I see no problem with both being fed from one transformer with adequate capacity but I guess it would be up to your AHJ & other authorities to call that "reliable"
 
Good point. I've run afoul of that one in the past. Reliability aside, just checking to see if I missed something that would prohibit two FPs from one xfmr.

Thanks!
 