Woobie
Member
- Location
- Los Angeles, CA
- Occupation
- Electrical Engineer
Does the NEC, NFPA 20, or common sense prohibit multiple Fire Pumps from being fed off a single service-tapped transformer? I know code want's a "dedicated feeder," but I'm not sure if this situation falls under that or some other clause that I'm not seeing.
More details on the situation:
There's an existing medium voltage service feeding a two-building campus. The service lineup has a separate tap + fused disconnect ahead of the main MV disconnect. That disconnect feeds a step-down transformer (in the same service lineup) and one existing Fire Pump.
Due to a site reconfiguration, there is now a need for two separate fire pumps (each feeding a separate building). We'd like to avoid using diesel fire pumps and definitely want to avoid tapping into the service bus. I'm wondering if it'd be allowed to - given physical feasibility - double-lug the FP transformer and provide a separate feeder from the transformer secondary to each fire pump controller (two total).
Thanks!
More details on the situation:
There's an existing medium voltage service feeding a two-building campus. The service lineup has a separate tap + fused disconnect ahead of the main MV disconnect. That disconnect feeds a step-down transformer (in the same service lineup) and one existing Fire Pump.
Due to a site reconfiguration, there is now a need for two separate fire pumps (each feeding a separate building). We'd like to avoid using diesel fire pumps and definitely want to avoid tapping into the service bus. I'm wondering if it'd be allowed to - given physical feasibility - double-lug the FP transformer and provide a separate feeder from the transformer secondary to each fire pump controller (two total).
Thanks!