Team,
After a lot of digging I'm not coming up with a clear answer. Hoping someone can assist.
Q: Can 2 fire pumps (or FP controller, ATS,) be on the same circuit breaker or should they have independent breakers.
INFO:
- My pumps are separate function (1 feeds hose stands, 1 feeds sprinklers). I know you want as few items inline that can break in the event of a fire.
- My pumps are fed by a single commercial breaker and single emergency breaker from the generators.
- Each pump has a dedicated ATS/controller
My thought is that you don't want a single breaker failing and taking out both pumps. Because during our annual FP test (run pumps and simulate commercial power loss, test ATS and breakers).....the EM breaker failed during transfer and both pumps failed to turn back on. Going to replace the breaker but it raised a question in my brain...
Thanks in advance, Neil
After a lot of digging I'm not coming up with a clear answer. Hoping someone can assist.
Q: Can 2 fire pumps (or FP controller, ATS,) be on the same circuit breaker or should they have independent breakers.
INFO:
- My pumps are separate function (1 feeds hose stands, 1 feeds sprinklers). I know you want as few items inline that can break in the event of a fire.
- My pumps are fed by a single commercial breaker and single emergency breaker from the generators.
- Each pump has a dedicated ATS/controller
My thought is that you don't want a single breaker failing and taking out both pumps. Because during our annual FP test (run pumps and simulate commercial power loss, test ATS and breakers).....the EM breaker failed during transfer and both pumps failed to turn back on. Going to replace the breaker but it raised a question in my brain...
Thanks in advance, Neil