Are you allowed to install 5 or 6 garage door openers on one 20 amp circuit?
Are you allowed to install 5 or 6 garage door openers on one 20 amp circuit?
Are you allowed to install 5 or 6 garage door openers on one 20 amp circuit?
Unless it's a fire station, I can't imagine them operating simultaneously.
Using remote controls you would not even need enough people to push all the buttons at once.But if nothing is installed to prevent someone from trying to open them at the same time can you use that arguement?
I don't remeber the max number of outlets on a 20 circuit in a garage. Each opener may need it's own outlet.
Sent from my LG-H870DS using Tapatalk
Thanks! Memory loss worries abated.Probably because there isn't a limit.
Unless a local amendment has one.
This can be taken two ways IMO.Where receptacles are used, 210.21(B)(2) says no. The table limits the load on a 20 amp branch circuit to 16 amps.
(2) Total Cord-and-Plug-Connected Load. Where connected
to a branch circuit supplying two or more receptacles or
outlets, a receptacle shall not supply a total cord-and-plug connected
load in excess of the maximum specified in Table
210.21(B)(2).
Are you allowed to install 5 or 6 garage door openers on one 20 amp circuit?
They can't afford the extra GFCI('s)I can't help asking why anyone with a six-car garage needs to be concerned with using an extra circuit for the openers?
This.I can't help asking why anyone with a six-car garage needs to be concerned with using an extra circuit for the openers?