keschaefer
Member
- Location
- Raleigh, NC
I had a comment come from an inspector that, under 225.30, a second generator may not be added to a building unless the existing generator is over 2000 A.
The facility has an existing generator (500kW) feeding Art. 700 and Art. 702 loads via separate ATSs. A second generator is being added to feed a UPS and associated HVAC loads (Art. 702) for a new data center area within the building. The building was originally designed for two generators and ATSs, only one was installed; this is an expansion project.
I read 225.30(A) as stating that "Additional feeders" may be added for any/all instance of the listed loads, with no limit.
The inspector is stating that since the first generator is less than 2000 A and is feeding one (or more) of the loads listed no additional feeders may be added.
Argument 2:
Article 225 II is for More Than One Building or Structure; there is only one building on this site fed by one utility transformer.
Thanks for your time.
The facility has an existing generator (500kW) feeding Art. 700 and Art. 702 loads via separate ATSs. A second generator is being added to feed a UPS and associated HVAC loads (Art. 702) for a new data center area within the building. The building was originally designed for two generators and ATSs, only one was installed; this is an expansion project.
I read 225.30(A) as stating that "Additional feeders" may be added for any/all instance of the listed loads, with no limit.
The inspector is stating that since the first generator is less than 2000 A and is feeding one (or more) of the loads listed no additional feeders may be added.
Argument 2:
Article 225 II is for More Than One Building or Structure; there is only one building on this site fed by one utility transformer.
Thanks for your time.