I've got someone telling me that for a combination light/fan mounted above a shower in a single family residence in California, there needs to be separate feed-through GFCI receptacles accessible in the bathroom for the fan part and the light part. This seems exceptionally silly to me. If there's a ground fault, I don't want the unit half live, I want it all dead. And making it even more silly, the entire circuit is on a Dual Function breaker that provides ground fault protection for personnel to the entire circuit.
I've searched high and low in the NEC, including looking at the California-specific requirements, and can't find anything to support this. Any idea where he might be getting this from?
210.8 mandates
410.10 mandates that luminaries directly over a bathtub or shower be marked suitable for damp or wet locations, but doesn't mention ground fault protection.
The only place I found a mandate for ground fault protection of a luminary located above a shower or tub is in 552.54 (B), which applies to "park trailers not covered fully under articles 510 or 511"
Ground fault protection is a very valuable safety measure, IMHO even more important than arc fault protection, but I don't see the advantage of, or requirement to provide it multiple times when it's already provided by the branch circuit breaker.
AHJ uses 2022 California Electrical Code, based on 2020 NEC.
I've searched high and low in the NEC, including looking at the California-specific requirements, and can't find anything to support this. Any idea where he might be getting this from?
210.8 mandates
but then goes on to only list requirements for GFCI protection for receptacles, not general outlets (such as lights or the exhaust fan). Elsewhere in the code, such as the requirements for arc fault breakers, it's pretty clear that the circuit breaker counts as "readily accessible".Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (F). The ground-fault circuit interrupter shall be installed in a readily accessible location.
410.10 mandates that luminaries directly over a bathtub or shower be marked suitable for damp or wet locations, but doesn't mention ground fault protection.
The only place I found a mandate for ground fault protection of a luminary located above a shower or tub is in 552.54 (B), which applies to "park trailers not covered fully under articles 510 or 511"
(B) Shower Luminaires. If a luminaire is provided over a bathtub or in a shower stall, it shall be of the enclosed and gasketed type and listed for the type of installation, and it shall be ground-fault circuit-interrupter protected.
Ground fault protection is a very valuable safety measure, IMHO even more important than arc fault protection, but I don't see the advantage of, or requirement to provide it multiple times when it's already provided by the branch circuit breaker.
AHJ uses 2022 California Electrical Code, based on 2020 NEC.