fmtjfw
Senior Member
- Location
- Fairmont, WV, USA
The following is from a code panel yesterday:
My grounding electrode system consists of a water pipe, a UFER, and a ground rod. My service conductors are 500kcmil copper. Can I run a 1/0 CU grounding electrode conductor to the water pipe, then a #4 copper conductor from the water pipe to the UFER, then a #6 copper from the UFER to the ground rod?
The answers were yes and no. What do you guys think?
My grounding electrode system consists of a water pipe, a UFER, and a ground rod. My service conductors are 500kcmil copper. Can I run a 1/0 CU grounding electrode conductor to the water pipe, then a #4 copper conductor from the water pipe to the UFER, then a #6 copper from the UFER to the ground rod?
The answers were yes and no. What do you guys think?