Multiple Grounding

Status
Not open for further replies.

ARNOL SMITH

New member
Does the code accept mutiple grounding points thru out a ELEMENTARY SCHOOL? We are bidding a school that has 21 ground rods located in 21 different areas of the school and bonded to the building steel. We also have a driven sround rod at each parking lot light pole. This is all tyed back to the main service ground with branch circuits and a ground wire in the conduit.
Is this accepable or is this illegal with multiple grounds?
 

NoVA Comms Power

Senior Member
Location
Alexandria, VA
ARNOL SMITH said:
Does the code accept mutiple grounding points thru out a ELEMENTARY SCHOOL? We are bidding a school that has 21 ground rods located in 21 different areas of the school and bonded to the building steel. We also have a driven sround rod at each parking lot light pole. This is all tyed back to the main service ground with branch circuits and a ground wire in the conduit.
Is this accepable or is this illegal with multiple grounds?
Sounds like the ground rod salesman had a good day. :rolleyes:

It's too bad the always-limited resources of education are being squandered in such a way.

The code does not prohibit adding additional supplemental ground rods to a grounding system (250.54) ...

Re: those light poles ... while I think that you described each pole as having it's own EGC, it wasn't clear ... so I feel it deserves restating here, if only for emphasis:

The "soil" can NOT serve as the required low-impedance fault-clearing path.

Step%20Voltage%20I%20.PNG



Step%20Voltage%20II%20.PNG
 
Last edited:

tom baker

First Chief Moderator
Staff member
I would be curious as to the reason. These ground rods are allowed per 250.54 but serve no usefull purpose. Can you do me a favor and if you get the bid ask the electrical designer what the purpose is, and what code or standard the requirements come from....
You could submit your bid with this as a deduction if not done....
 