Since the 2020 code is going to require outside disconnects on dwellings, I want to setup a new main service so it is easy to convert it to a subpanel instead of a main panel (it is being installed under 2017 code so it can still be a Service). I want to add a separate equipment ground bar in the panel and run all equipment grounds to it. Just bolting the bar to the panel is sufficient for equipment grounding with the main bonding jumper connecting the neutral bar to the panel enclosure. But I've never liked relying on screws for equipment ground bars and would like to run a #6 copper jumper from the neutral bar to that equipment grounding bar.
Is that legal? This #6 cu jumper is effectively paralleling the main bonding jumper. Can you have more than one main bonding jumper? Even if it is legal, do you think it is a bad idea? I think the factory one needs to stay since it is a green screw. I know the ground electrode conductor must go the grounded neutral bar and cannot go to the equipment ground bar.
Is that legal? This #6 cu jumper is effectively paralleling the main bonding jumper. Can you have more than one main bonding jumper? Even if it is legal, do you think it is a bad idea? I think the factory one needs to stay since it is a green screw. I know the ground electrode conductor must go the grounded neutral bar and cannot go to the equipment ground bar.