On a two family dwelling I've added a third meter socket for common areas. The existing entrance conductors are 3/0 and feed a single buss dual meter panel. The service conductors to the new meter are 4 AWG and are connected to the end of the existing entrance conductors (in series). The service entrance conductors are never in parallel.
The reason I mention that is that I'm not sure if this constitutes multiple sets of service entrance conductors. I also have another reference, designed to clarify the NEC, that says that 250.66 note 1 applies to service entrance conductors in parallel and I'm having trouble interpreting it one way or the other myself.
I have to go 150' to tie the water pipe to the electrode system so I'd certainly rather use 4 AWG than 2 AWG.
The reason I mention that is that I'm not sure if this constitutes multiple sets of service entrance conductors. I also have another reference, designed to clarify the NEC, that says that 250.66 note 1 applies to service entrance conductors in parallel and I'm having trouble interpreting it one way or the other myself.
I have to go 150' to tie the water pipe to the electrode system so I'd certainly rather use 4 AWG than 2 AWG.