I am working on an old commercial building that is being converted to underground service. We are installing all new 400A service, meters, feeders, and subs. I am questioning my boss on the grounding of he service.
We have a 4" PVC conduit (service lateral) going into a termination cabinet. From those lugs, we are taking 500MCM in to a "Bus Duct". Below this are 2 meter/mains, a 100A and a 200A and space for a future 3rd meter main. These meter mains are actually bolted to the bus duct. There is no conduit between them. It is setup for this from B-Line. So they are essentially the same box once they are totally bolted together. Boss wants to connect ground rod and the bus duct enclosure to the neutral bus bar in the bus duct. he wants to leave the meter/mains G-N bonded as well.
I think this is wrong because some of the neutral current will split at the meter/main bonds and go through the enclosures back to the bonding jumper in the bus duct. Am I right? I've never done a service with mor than one meter, so I am unsure of this.
Thanks, this is an awesome forum.
Mike
[ April 29, 2004, 10:08 PM: Message edited by: mhulbert ]
We have a 4" PVC conduit (service lateral) going into a termination cabinet. From those lugs, we are taking 500MCM in to a "Bus Duct". Below this are 2 meter/mains, a 100A and a 200A and space for a future 3rd meter main. These meter mains are actually bolted to the bus duct. There is no conduit between them. It is setup for this from B-Line. So they are essentially the same box once they are totally bolted together. Boss wants to connect ground rod and the bus duct enclosure to the neutral bus bar in the bus duct. he wants to leave the meter/mains G-N bonded as well.
I think this is wrong because some of the neutral current will split at the meter/main bonds and go through the enclosures back to the bonding jumper in the bus duct. Am I right? I've never done a service with mor than one meter, so I am unsure of this.
Thanks, this is an awesome forum.
Mike