Here's the situation. I've got a building (industrial establishment) where the motors in the building are to be fed from another MCC building 300 or so feet away. The motor loads in question are for hot water unit heaters. The motors are 480V with a local control station and all around 1/2 HP.
I've got 8 of these motors and their associated three wire control circuits. They're also located in a Class 1 Div 2 location, thus the remote MCC. If I'm reading 725.48 (B) (1) (2008) correctly I would be required to have 8 separate conduits, one for each motor and the associated controls. Am I missing something here? Is there a way to combine some of these and avoid so much conduit?
I've got 8 of these motors and their associated three wire control circuits. They're also located in a Class 1 Div 2 location, thus the remote MCC. If I'm reading 725.48 (B) (1) (2008) correctly I would be required to have 8 separate conduits, one for each motor and the associated controls. Am I missing something here? Is there a way to combine some of these and avoid so much conduit?