cvirgil467
Senior Member
- Location
- NewYork
Question on conductor sizing and OCPD sizing to a VFD with bypass that is operating more than 1 motor.
For conductor sizing to VFD - is this based on 430.24 (125% of largest motor plus sum of the other motors) or 430.122(B)(2) (125% of motor full load rating - I assume this means the sum of all motors combined x 125%)
For overcurrent protection to the VFD - based on size per 430.53(C)?
Thanks.